Detached Garage Wiring Questions

I just installed a 28x36 pole barn that’s about 70’ away from my house and it’s another 70’ to my main breaker panel within my basement. I ran 2” schedule 40 conduit a minimum of 2’ deep with a sweep at the house to an LB fitting for entry into the house. I plan to continue the 2’ conduit along the wall adjacent to the finished ceiling. My main panel has plenty of capacity for a 100 amp service to the garage. The primary draw at the garage will be:

20 amp Rotary lift
20 amp welder
15 amp compressor
15 amp sewer sump

+ lighting.
I believe I need 1/0-1/0-1/0-2 aluminum
Or 1-1-1-4
THHN or THWN for the distance and required Amps

Copper is about four times more expensive than aluminum.

What are the thoughts of electricians on this board regarding my plans?

Thanks












Last edited by allyolds68; November 23rd, 2018 at 07:59 AM.
allyolds68 is offline  
Old November 23rd, 2018, 08:40 AM
  #2  
Registered User
 
OLDSter Ralph's Avatar
 
Join Date: Sep 2017
Location: St. Paul Minnesota
Posts: 4,014
Well, a good electrician knows the electrical codes..... The codes are there for safety. If you consulted a qualified electrician and he told you what to do and what to use, then you should be fine. I believe that copper will carry more electricity than aluminum. Arc fault and GFCI's might be required in your area.
You obviously made an investment in the pole building. Now make an investment in the electrical. It might be a good investment to have a licensed electrician make the final power connections. If something is not right with your installation or something is wrong when its powered up, the electrician on hand can quickly diagnose it.
........Just my two cents worth
OLDSter Ralph is offline  
Old November 23rd, 2018, 09:30 AM
  #3  
Administrator
 
oldcutlass's Avatar
 
Join Date: Oct 2009
Location: Poteau, Ok
Posts: 40,553
Single 0 for aluminum or 2ga for copper. Wire size needs to be rated for 120% minimum of your load. Since your not going over 300 ft, voltage drop is not an issue. Your conduit size is adequate.
oldcutlass is online now  
Old November 23rd, 2018, 10:21 AM
  #4  
Registered User
Thread Starter
 
allyolds68's Avatar
 
Join Date: Jul 2008
Location: Seneca Falls, NY
Posts: 5,258
Originally Posted by oldcutlass
Single 0 for aluminum or 2ga for copper. Wire size needs to be rated for 120% minimum of your load. Since your not going over 300 ft, voltage drop is not an issue. Your conduit size is adequate.
thank you

i haven’t talked to an electrician but I can research fairly well. I appreciate you reviewing it. Would you spend the extra money for copper?

also because this is underground the ground has to be shielded wire as well, correct?

Last edited by allyolds68; November 23rd, 2018 at 10:30 AM.
allyolds68 is offline  
Old November 23rd, 2018, 01:19 PM
  #5  
Administrator
 
oldcutlass's Avatar
 
Join Date: Oct 2009
Location: Poteau, Ok
Posts: 40,553
I would pull 2 load and 1 neutral of the whatever size your using and a #8 ground. I don't know about the shielding part, have never done it here.
oldcutlass is online now  
Old November 23rd, 2018, 05:51 PM
  #6  
CH3NO2 LEARN IT BURN IT
 
droldsmorland's Avatar
 
Join Date: Jul 2010
Location: Land of Taxes
Posts: 4,842
Nice Mike! Pulled the trigger just in time for the weather too. IMO I'd personally avoid aluminum. I know the price is tempting but it's not worth it. The aluminum gets brittle much faster than copper. The aluminum wires expansion rate is exponentially higher than copper. The propensity to loosen up under the lugs goes up and cause all sorts of resistance and hotspot even arching in extreme cases. Don't skimp on the sub-panel and breakers. Every time I have to repair a service or a distribution system which has aluminum I curse the installer.
You might want to recalc the additive load again in preparation for future add-ons once the wife moves you out there full time. I see a working fluid fridge, big screen, sound, heat and AC in the future? Run a spare schedule 40 out there for PEX piping....Like how Im spending your money...hehe. Stay warm...Steve
droldsmorland is offline  
Old November 23rd, 2018, 07:54 PM
  #7  
Registered User
 
classicmuscle442's Avatar
 
Join Date: Sep 2012
Location: Water Wonderland MI.
Posts: 1,414
If installed correctly the metal conduit can be used as the ground, just bond a ground wire to the metal junction boxes. National electric code, local codes may be different.
classicmuscle442 is offline  
Old November 23rd, 2018, 08:33 PM
  #8  
Registered User
 
OLDSter Ralph's Avatar
 
Join Date: Sep 2017
Location: St. Paul Minnesota
Posts: 4,014
Originally Posted by droldsmorland
Nice Mike! Pulled the trigger just in time for the weather too. IMO I'd personally avoid aluminum. I know the price is tempting but it's not worth it. The aluminum gets brittle much faster than copper. The aluminum wires expansion rate is exponentially higher than copper. The propensity to loosen up under the lugs goes up and cause all sorts of resistance and hotspot even arching in extreme cases. Don't skimp on the sub-panel and breakers. Every time I have to repair a service or a distribution system which has aluminum I curse the installer.
You might want to recalc the additive load again in preparation for future add-ons once the wife moves you out there full time. I see a working fluid fridge, big screen, sound, heat and AC in the future? Run a spare schedule 40 out there for PEX piping....Like how Im spending your money...hehe. Stay warm...Steve
I would use the copper, myself. And future loads such as heat and A/C are realistic additions that should be a consideration now. A gas line for winter heat is not such a crazy idea, either. Its an investment that won't hurt resale value.


OLDSter Ralph is offline  
Old November 23rd, 2018, 09:15 PM
  #9  
1971 442 conv
 
Texas442's Avatar
 
Join Date: Jun 2009
Location: Austin, Texas
Posts: 665
trench

You may have already thought about this. If your local codes allows running a second smaller conduit in the same trench, then you may want to consider running 2 shielded CAT5 or better Ethernet cables. One for router extender and one for a camera.
Texas442 is offline  
Related Topics
Thread
Thread Starter
Forum
Replies
Last Post
11971four4two
Miscellaneous Classifieds
4
January 21st, 2022 12:24 PM
69442murph
Miscellaneous Classifieds
0
January 30th, 2019 10:55 AM
mpolds
Miscellaneous Classifieds
0
November 10th, 2018 10:11 PM
eds
The Clubhouse
27
October 16th, 2013 05:33 AM
68Tom
Miscellaneous Classifieds
0
July 24th, 2012 10:34 AM



Quick Reply: Detached Gara



All times are GMT -7. The time now is 04:16 PM.